Hello everyone, well ive asked multiple people I know this question and I either get the run around or they just don't know the answer I'm hoping maybe someone on here could help me. The compressor station I operate I have two Cat G3306TA's with 175kw 480v three phase Cat generators I run one as prime power and one as standby alternating them every 45 days of runtime. They supply all power for everything onsite such as the operators shack, the stadium lights for the site, miles and miles of electric heat trace, and the hot start circulation heaters for the compressors and engines oil and coolant. Alternating current isn't really my strong point but I don't feel that something is right here, on the generator control panel I'm showing around 60 amps of draw on the second and third legs of the three phase and around 30 amps of draw on the first leg, My voltage on the first leg is right at 480 but on the second and third legs its around 450volts or less depending on ambient temperature the draw goes up and those voltages drop more because the heat trace is self regulating. The heat trace runs constantly which is single phase and the hotstarts which are three phase only run when a compressor is shut down. Ive heard that its not good on the generators to have an unbalanced load and the generator controller has some shutdown setpoints for unbalanced load which ive had to move higher to keep them running so that confirms to me that somethings wrong. Ive also had issues recently when I switch one of the hotstarts on it will trip the circuit breaker for that hot start or it will trip the motor protection switch in the hotstart control box. I'm assuming its just like DC where when your voltage drops your amperage draw goes up so I'm guessing due to the lessened voltage on the two legs its the cause of tripping the breakers and motor protection switches on the hotstarts.

My question is I guess is it normal on an unbalanced load like this to have the voltage lower on the legs with the higher load or is it something in the generator not controlling the voltage like it should? Will it hurt the generator ro run like this and if so what is the effect? What will the unbalanced three phase do to the things that run three phase on site like the hotstarts? How do I balance the load if possible? Also how do I tell if the three phase is WYE or Delta as the heating elements in the hotstarts have some jumper bars that you move around depending on the configuration.

Thanks Guys!
Caterpillar 30 PS244
International Harvester T-40
John Deere 720 Diesel
Please log in or create an account to join the conversation.
Wed, Jan 6, 2016 11:02 PM
mrsmackpaul
Offline
Send a private message to mrsmackpaul
Posts: 1,456
Thank you received: 0
do you have the same problem with each generator ??

voltage is directly proportional to the amps (current)

should be able to run fine with a unbalanced load as long as the load doesnt exceed the maximum of any phase of the genny

the unbalanced load will have effect on three phase equipment but and its big but your unbalanced supply will have a big effect your supply has to be right and its not real flash

It isnt normal to have a unbalanced supply but you will never have a balanced load even if you ran mainly 3 phase gear off it the control circuitry is still single or 2 phase so you never have a balanced load
power supply coming down your street is balanced and the voltages are the same across the phases yet the loads are not balanced and change constantly across the phases as people turn things on and off

dunno what your talking about with hot starts ???? star and delta on a motor if the terminal block is ok for, star the three bars are at the bottom or top three studs, for delta the three bars are on running vertically on the studs

dunno if any of this helps but your problem is more of a supply problem than anything else as in a genny problem

Paul
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 2:20 AM
wimmera farmer
Offline
Send a private message to wimmera farmer
Posts: 447
Thank you received: 1
Reply to mrsmackpaul:
do you have the same problem with each generator ??

voltage is directly proportional to the amps (current)

should be able to run fine with a unbalanced load as long as the load doesnt exceed the maximum of any phase of the genny

the unbalanced load will have effect on three phase equipment but and its big but your unbalanced supply will have a big effect your supply has to be right and its not real flash

It isnt normal to have a unbalanced supply but you will never have a balanced load even if you ran mainly 3 phase gear off it the control circuitry is still single or 2 phase so you never have a balanced load
power supply coming down your street is balanced and the voltages are the same across the phases yet the loads are not balanced and change constantly across the phases as people turn things on and off

dunno what your talking about with hot starts ???? star and delta on a motor if the terminal block is ok for, star the three bars are at the bottom or top three studs, for delta the three bars are on running vertically on the studs

dunno if any of this helps but your problem is more of a supply problem than anything else as in a genny problem

Paul
If the single phase load can be split into three fairly equal load circuits and one of each phase it will fix your issues permanently. Have known some to run a couple of big lights off one phase to balance the load. That sparky stuff bites, be careful where you poke you nose into it. Don't let the smoke out. cheers WF
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 3:34 AM
sdmuleman
Offline
Send a private message to sdmuleman
Posts: 174
Thank you received: 0
Reply to mrsmackpaul:
do you have the same problem with each generator ??

voltage is directly proportional to the amps (current)

should be able to run fine with a unbalanced load as long as the load doesnt exceed the maximum of any phase of the genny

the unbalanced load will have effect on three phase equipment but and its big but your unbalanced supply will have a big effect your supply has to be right and its not real flash

It isnt normal to have a unbalanced supply but you will never have a balanced load even if you ran mainly 3 phase gear off it the control circuitry is still single or 2 phase so you never have a balanced load
power supply coming down your street is balanced and the voltages are the same across the phases yet the loads are not balanced and change constantly across the phases as people turn things on and off

dunno what your talking about with hot starts ???? star and delta on a motor if the terminal block is ok for, star the three bars are at the bottom or top three studs, for delta the three bars are on running vertically on the studs

dunno if any of this helps but your problem is more of a supply problem than anything else as in a genny problem

Paul
Seems reasonable to me that if there's about half the load on one leg the voltage on that would be higher.

Sounds like it's hooked up with all of the 1 phase loads on one leg which isn't optimal - they should be distributed more or less evenly on all 3.

I'm not an expert by any means, but I fell like I've heard before that it's not good to have the machine that much out of load balance. I think some unbalance isn't a big issue, but if it's enough that you're seeing a voltage drop like that it's probably something that should be fixed.

Having to adjust the alarm points is worrying though since this would indicate things are changing to cause the unbalance - have they been rewiring or something that would shift loads around?
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 3:34 AM
dieselfreakcjw
Topic Author
Offline
Send a private message to dieselfreakcjw
Posts: 91
Thank you received: 0
Reply to sdmuleman:
Seems reasonable to me that if there's about half the load on one leg the voltage on that would be higher.

Sounds like it's hooked up with all of the 1 phase loads on one leg which isn't optimal - they should be distributed more or less evenly on all 3.

I'm not an expert by any means, but I fell like I've heard before that it's not good to have the machine that much out of load balance. I think some unbalance isn't a big issue, but if it's enough that you're seeing a voltage drop like that it's probably something that should be fixed.

Having to adjust the alarm points is worrying though since this would indicate things are changing to cause the unbalance - have they been rewiring or something that would shift loads around?
Hello everybody thank you for the inputs, I was hoping it would be more of a distribution problem than a supply problem as mrsmackpaul said and I believe its true, I talked with another company today and they said to try the same thing you mentioned which was try firing up the spare generator and seeing if the voltage differential shows up as well, he says if the voltage regulator in the gen is set up to only monitor a certain leg in the gen then that leg will have correct voltage but the others will not he says the best bet is to try and balance the load which may be easier than I thought. I originally believed that you used two legs of the gen to make single phase but after looking at Wikipedia it says the best way to pull single off of a three phase gen is to run it in a wye configuration where you only take one leg of the gen and a neutral and transform it down to the required voltage so it should be fairly straight forward I think just moving some of the heat trace circuits around between the different transformers. The guy also said that you could get a different voltage regulator or convert the current one to a three phase sensing VR and it will make an average voltage of all three legs where in one may be 490v and the other two may be 470v instead of the current configuration with one leg at 480v and the other two at 440-450v. This is a hotstart http://www.hotstart.com/assets/Data-Sheets/Data-sheet-OCLE-DS-OCLE-E.pdf for those that were curious. Its a pump, 480v 3ph motor, and 480v 3ph electric heating element combo what it does is when one of the compressors is shutdown be it either a fault or normal maintenance, the hotstart is turned on automatically by a relay and it begins to recirculate the engine oil and the coolant (separate pumps motors and elements for each) through the engine and through control circuitry it maintains them at a set temperature 120 deg f for coolant and 100 deg f for oil, this is to allow for easier startup and to ensure that at startup oil gets where it needs to go as quickly as possible. I had read somewhere today not to run three phase motors on more than a 2% imbalance which at our current configuration I have an 8% imbalance so now it makes sense why ive been seeing motor protection switches being popped and the lack of voltage therefore more amperage explains the breakers being tripped. This stuff makes me nervous ha ha ive been bitten by 120v before I cant imagine what 480v would do. This problem all arose a couple years ago when the customer decided to add electric heat trace to the rest of their process gas piping and I mean lots of it, I think the eletricians went through several rolls of it probably thousands of feet and just no one has bothered to look into it the customer owns the generators and I just maintain them and it hard to convince them to change anything since "its been working that way for a while now why change it". Thanks for all the input guys its kinda fun learning this stuff.
Caterpillar 30 PS244
International Harvester T-40
John Deere 720 Diesel
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 9:52 AM
drujinin
Offline
Send a private message to drujinin
Posts: 3,852
Thank you received: 0
Reply to dieselfreakcjw:
Hello everybody thank you for the inputs, I was hoping it would be more of a distribution problem than a supply problem as mrsmackpaul said and I believe its true, I talked with another company today and they said to try the same thing you mentioned which was try firing up the spare generator and seeing if the voltage differential shows up as well, he says if the voltage regulator in the gen is set up to only monitor a certain leg in the gen then that leg will have correct voltage but the others will not he says the best bet is to try and balance the load which may be easier than I thought. I originally believed that you used two legs of the gen to make single phase but after looking at Wikipedia it says the best way to pull single off of a three phase gen is to run it in a wye configuration where you only take one leg of the gen and a neutral and transform it down to the required voltage so it should be fairly straight forward I think just moving some of the heat trace circuits around between the different transformers. The guy also said that you could get a different voltage regulator or convert the current one to a three phase sensing VR and it will make an average voltage of all three legs where in one may be 490v and the other two may be 470v instead of the current configuration with one leg at 480v and the other two at 440-450v. This is a hotstart http://www.hotstart.com/assets/Data-Sheets/Data-sheet-OCLE-DS-OCLE-E.pdf for those that were curious. Its a pump, 480v 3ph motor, and 480v 3ph electric heating element combo what it does is when one of the compressors is shutdown be it either a fault or normal maintenance, the hotstart is turned on automatically by a relay and it begins to recirculate the engine oil and the coolant (separate pumps motors and elements for each) through the engine and through control circuitry it maintains them at a set temperature 120 deg f for coolant and 100 deg f for oil, this is to allow for easier startup and to ensure that at startup oil gets where it needs to go as quickly as possible. I had read somewhere today not to run three phase motors on more than a 2% imbalance which at our current configuration I have an 8% imbalance so now it makes sense why ive been seeing motor protection switches being popped and the lack of voltage therefore more amperage explains the breakers being tripped. This stuff makes me nervous ha ha ive been bitten by 120v before I cant imagine what 480v would do. This problem all arose a couple years ago when the customer decided to add electric heat trace to the rest of their process gas piping and I mean lots of it, I think the eletricians went through several rolls of it probably thousands of feet and just no one has bothered to look into it the customer owns the generators and I just maintain them and it hard to convince them to change anything since "its been working that way for a while now why change it". Thanks for all the input guys its kinda fun learning this stuff.
Balance the single phase loads(heat trace) across all three phases as this will cure the problem properly. Switching from a single phase sensing to a three phase sensing will raise your voltage average(true). But it is only a bandaid not a cure! We run the 3512/16 gensets on load banks with a couple of percent imbalance because the resistance across the phases very based on age and abuse. Some customers don't like to see it with varying currents and output voltages but we are usually within 1% for voltage.
Typically CAT(KATO) generators are 277/480 Wye on the busbars so that a neutral can be generated.
The Hot Start doesn't care if its a Delta or a Wye as long as its getting 480Vac. Are these the big ones that do oil and water or the small ones mounted on the side of the skid that only do water? I run some on GE locomotive engines(3.5 MW) that are 5kw on Oil and 10kw on Water. Those babies will suck power but heat the engine Quick!
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 10:25 AM
ccjersey
Offline
Send a private message to ccjersey
Posts: 4,422
Thank you received: 0
Don't think there is any practical advantage to tapping line to neutral for single phase (277 volt) vs line to line (480 volt). Just as effective (and easier if you have 480 transformers already) to simply balance the loads across the 3 phases by adding additional transformers that tap the lightly loaded phase. For example there may be a single transformer tapped on phases A and B that feeds all the heat trace and other single phase loads. Adding 2 more single phase or a single 3 phase transformer so load is tapped on A and B, B and C, A and C should go a long way to resolving your voltage problem.

The reconfigurable hot starts probably are intended to change the voltage requirement of the hot starts themselves, not be adjusted for the generator being configured as either Y or Delta. In almost every situation, a generator can be considered a "black box" that produces the desired voltage at the desired frequency. Doesn't matter whether it is Y or delta as long as it makes 480 3 phase 60 Hz. ........... unless you need 277.......then it has to be Y......or you have to have a transformer.
D2-5J's, D6-9U's, D318 and D333 power units, 12E-99E grader, 922B & 944A wheel loaders, D330C generator set, DW20 water tanker and a bunch of Jersey cows to take care of in my spare time😄
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 10:32 AM
ronm
Offline
Send a private message to ronm
Posts: 1,143
Thank you received: 0
Reply to ccjersey:
Don't think there is any practical advantage to tapping line to neutral for single phase (277 volt) vs line to line (480 volt). Just as effective (and easier if you have 480 transformers already) to simply balance the loads across the 3 phases by adding additional transformers that tap the lightly loaded phase. For example there may be a single transformer tapped on phases A and B that feeds all the heat trace and other single phase loads. Adding 2 more single phase or a single 3 phase transformer so load is tapped on A and B, B and C, A and C should go a long way to resolving your voltage problem.

The reconfigurable hot starts probably are intended to change the voltage requirement of the hot starts themselves, not be adjusted for the generator being configured as either Y or Delta. In almost every situation, a generator can be considered a "black box" that produces the desired voltage at the desired frequency. Doesn't matter whether it is Y or delta as long as it makes 480 3 phase 60 Hz. ........... unless you need 277.......then it has to be Y......or you have to have a transformer.
Yes, do not get careless with that 480, it can hurt you bad...an electrician working on a pellet mill one told me you can't leave a screwdriver burr on a screw, it will start an arc...
That pellet mill was the only big genset I've ever worked around, I mainly took care of the engine-a 16V71 Detroit...loved that motor.
Electricity-wise, I'm OK up to 24V, above that I leave it to the experts...
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 10:56 AM
dieselfreakcjw
Topic Author
Offline
Send a private message to dieselfreakcjw
Posts: 91
Thank you received: 0
Reply to drujinin:
Balance the single phase loads(heat trace) across all three phases as this will cure the problem properly. Switching from a single phase sensing to a three phase sensing will raise your voltage average(true). But it is only a bandaid not a cure! We run the 3512/16 gensets on load banks with a couple of percent imbalance because the resistance across the phases very based on age and abuse. Some customers don't like to see it with varying currents and output voltages but we are usually within 1% for voltage.
Typically CAT(KATO) generators are 277/480 Wye on the busbars so that a neutral can be generated.
The Hot Start doesn't care if its a Delta or a Wye as long as its getting 480Vac. Are these the big ones that do oil and water or the small ones mounted on the side of the skid that only do water? I run some on GE locomotive engines(3.5 MW) that are 5kw on Oil and 10kw on Water. Those babies will suck power but heat the engine Quick!
Well we have three different transformers up there ill have to look into whether we can hook up to all three different legs or not as ccjersey mentioned and hopefully we can get this problem rectified (ha ha electrical pun). I agree with you on the three phase sensing VR that it is just a bandaid and in my opinion the customers money wasted. I was looking at the tags for these gens the other day and it said they were a 12 wire wye series (not sure on the series). does it damage the generator to run it imbalanced? Are you guys selling your power or just using it local? The instructions for the heating elements in the hotstarts say they are configurable for wye or delta what would be the reasoning there? Yeah they are pretty big they use a 3/4hp motor on coolant with a 30kw element and a 1hp motor for oil with a 9kw element, and then the compressors use a 1hp motor with a 6kw element, with just a couple of them running it'll definitely make one generator grunt, if all 8 are going (4 engine 4 compressor) when we have a plant outage etc its kinda cool to watch it trigger the load dependent start stop in the controller. Itll automatically start, parallel, and load the second generator and boy are they giving it everything they got. The controller is two woodward easygen 3000's with woodward 2301a governors the customer installed the panel when we added the second generator in 2013. [quote="drujinin"]Balance the single phase loads(heat trace) across all three phases as this will cure the problem properly. Switching from a single phase sensing to a three phase sensing will raise your voltage average(true). But it is only a bandaid not a cure! We run the 3512/16 gensets on load banks with a couple of percent imbalance because the resistance across the phases very based on age and abuse. Some customers don't like to see it with varying currents and output voltages but we are usually within 1% for voltage.
Typically CAT(KATO) generators are 277/480 Wye on the busbars so that a neutral can be generated.
The Hot Start doesn't care if its a Delta or a Wye as long as its getting 480Vac. Are these the big ones that do oil and water or the small ones mounted on the side of the skid that only do water? I run some on GE locomotive engines(3.5 MW) that are 5kw on Oil and 10kw on Water. Those babies will suck power but heat the engine Quick![/quote]
Caterpillar 30 PS244
International Harvester T-40
John Deere 720 Diesel
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 11:19 AM
dieselfreakcjw
Topic Author
Offline
Send a private message to dieselfreakcjw
Posts: 91
Thank you received: 0
Reply to ccjersey:
Don't think there is any practical advantage to tapping line to neutral for single phase (277 volt) vs line to line (480 volt). Just as effective (and easier if you have 480 transformers already) to simply balance the loads across the 3 phases by adding additional transformers that tap the lightly loaded phase. For example there may be a single transformer tapped on phases A and B that feeds all the heat trace and other single phase loads. Adding 2 more single phase or a single 3 phase transformer so load is tapped on A and B, B and C, A and C should go a long way to resolving your voltage problem.

The reconfigurable hot starts probably are intended to change the voltage requirement of the hot starts themselves, not be adjusted for the generator being configured as either Y or Delta. In almost every situation, a generator can be considered a "black box" that produces the desired voltage at the desired frequency. Doesn't matter whether it is Y or delta as long as it makes 480 3 phase 60 Hz. ........... unless you need 277.......then it has to be Y......or you have to have a transformer.
[quote="ccjersey"]Don't think there is any practical advantage to tapping line to neutral for single phase (277 volt) vs line to line (480 volt). Just as effective (and easier if you have 480 transformers already) to simply balance the loads across the 3 phases by adding additional transformers that tap the lightly loaded phase. For example there may be a single transformer tapped on phases A and B that feeds all the heat trace and other single phase loads. Adding 2 more single phase or a single 3 phase transformer so load is tapped on A and B, B and C, A and C should go a long way to resolving your voltage problem.

The reconfigurable hot starts probably are intended to change the voltage requirement of the hot starts themselves, not be adjusted for the generator being configured as either Y or Delta. In almost every situation, a generator can be considered a "black box" that produces the desired voltage at the desired frequency. Doesn't matter whether it is Y or delta as long as it makes 480 3 phase 60 Hz. ........... unless you need 277.......then it has to be Y......or you have to have a transformer.[/quote]

Oooh ok now it makes sense, I thought you were constrained to pulling off of either A-B, B-C which would leave us in the same boat we're already in, I never thought of pulling from A-C, we have three different transformers ill have to look how its all configured if we can actually do it with the existing setup or if we need to add another transformer. As for the hotstart configuration the heating elements are a fixed 480 but you can move some jumper bars around if its wye or delta, I'm not sure how much of a difference it will make? Man this three phase stuff is confusing with so many different variations and combinations :tape: Thank you for clearing that up sir.
Caterpillar 30 PS244
International Harvester T-40
John Deere 720 Diesel
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 11:28 AM
dieselfreakcjw
Topic Author
Offline
Send a private message to dieselfreakcjw
Posts: 91
Thank you received: 0
Reply to ronm:
Yes, do not get careless with that 480, it can hurt you bad...an electrician working on a pellet mill one told me you can't leave a screwdriver burr on a screw, it will start an arc...
That pellet mill was the only big genset I've ever worked around, I mainly took care of the engine-a 16V71 Detroit...loved that motor.
Electricity-wise, I'm OK up to 24V, above that I leave it to the experts...
[quote="ronm"]Yes, do not get careless with that 480, it can hurt you bad...an electrician working on a pellet mill one told me you can't leave a screwdriver burr on a screw, it will start an arc...
That pellet mill was the only big genset I've ever worked around, I mainly took care of the engine-a 16V71 Detroit...loved that motor.
Electricity-wise, I'm OK up to 24V, above that I leave it to the experts...[/quote]

Oh wow that's pretty crazy I can believe it I guess, anything that would bring the voltage closer to a ground and let it jump. Pellet mill as in for wood pellets? These are pretty small generators but I'm in the same boat you were in I just maintain the engines but this unbalanced issue has caused me some problems and the customer doesn't really seem to care so I guess I'm just trying to educate myself enough to be able to explain to them the problems it causes and their electricians aren't experienced with generators which is probably why this problem even exists but hopefully I get them to fix it. I'm kinda curious as well its pretty interesting stuff but most of it is way over my head. a 16v71 is a pretty darn big engine how many hp is that?
Caterpillar 30 PS244
International Harvester T-40
John Deere 720 Diesel
Please log in or create an account to join the conversation.
Thu, Jan 7, 2016 11:44 AM
Showing 1 to 10 of 44 results
1
YouTube Video Placeholder

Follow Us on Social Media

Our channel highlights machines from the earliest Holt and Best track-type tractors, equipment from the start of Caterpillar in 1925, up to units built in the mid-1960s.

Upcoming Events

CAFES 2025 TULARE, CALIFORNIA

Chapter Fifteen

| Tulare, California

Wheatlands Warracknabeal Easter Rally

Chapter Nineteen

| 34 Henty Hwy, Warracknabeal

Veerkamp Open House 2025

Chapter Fifteen

| Placerville, CA

HAMILTON PASTURAL MUSEUM

Chapter Nineteen

| Cnr Hiller Lane and Ballarat Road, Hamilton, Vic, 3300
View Calendar
ACMOC

Antique Caterpillar
Machinery Owners Club

1115 Madison St NE # 1117
Salem, OR 97301

[email protected]

Terms & Privacy
Website developed by AdCo

Testimonials

"I became a member recently because the wealth of knowledge here is priceless." 
-Chris R

Join Today!