Ok, all you gen savvy folk. The farm has a Onan gen, 1970's 6cyl turbo Allis. Brushless! I had to remove the excitation field coils/end bell to change a bearing that was destroyed. Now the engine runs fine, the terrible grinding noise is gone, but there isn't any output. The rotor has a few diodes that I haven't tried to check, and I haven't tried to check continuity of the excitation field coil. Any Ideas? I will post some pics later. Thanks for your thoughts
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 1:23 AM
WA7OPY
Offline
Send a private message to WA7OPY
Posts: 217
Thank you received: 0
Did the exciter rotor rub the exciter field poles??? If so you will need to make friends with a motor rewind shop....WA7OPY
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 7:29 AM
ccjersey
Offline
Send a private message to ccjersey
Posts: 4,422
Thank you received: 0
Check for "residual" voltage on the output. Should be some AC voltage output from the stator windings before any output breaker etc. Usually anything over a few volts will build up if everything else is good. 0 or just a few volts you need to flash the field to boost it up. Many Onan manuals will have the procedure. Basically match polarity at connections to the exciter field leads and apply DC there. A 6 volt dry cell is plenty or I have used the smallest voltage I can get out of the generator starting batteries THROUGH a probe type test light so the lamp limits current flowing. In an emergency you can just scratch a wire on the terminals with the generator turning at full governed rpm and get it to go.

I am guessing you lost the residual from the vibrations resulting from the bad bearing or might have swapped the exciter field leads when reinstalling it and simply need to flash it.

If you have good residual or flashing doesn't cause voltage to build up AND STAY UP, then the other checks you mentioned need to be done. The exciter field or rotor or the main field on the rotor may be shorted from the parts scrubbing. disconnect the field from the rectifier heat sinks and test. If those are ok, the rectifier diodes will be arranged in two groups of 3 all same polarity and are usually stud mount type so you can easily replace them. To test each one you can remove the stud end from the heat sink. I replaced all three when I found any one bad. They are available from suppliers like DIGIKEY and MOUSER, sometimes eBay etc. Mainly match up the stud size and polarity and most any amperage and voltage will work and be better than what was originally installed. I think I wound up with 40 amp and 400 volt on an 85KR I fixed once.

OH......before you do all this, check the exciter breaker on the control panel isn't tripped. That would be can easy fix, but it may have tripped for a reason. If you need more troubleshooting, I can supply ONAN literature or its probably available online if you search for ONAN 900-0150 Service manual The wingspan site pdf file is what you want.
D2-5J's, D6-9U's, D318 and D333 power units, 12E-99E grader, 922B & 944A wheel loaders, D330C generator set, DW20 water tanker and a bunch of Jersey cows to take care of in my spare time😄
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 8:17 AM
bursitis
Offline
Member
Send a private message to bursitis
Location: Oklahoma
Posts: 1,085
Thank you received: 4
Reply to ccjersey:
Check for "residual" voltage on the output. Should be some AC voltage output from the stator windings before any output breaker etc. Usually anything over a few volts will build up if everything else is good. 0 or just a few volts you need to flash the field to boost it up. Many Onan manuals will have the procedure. Basically match polarity at connections to the exciter field leads and apply DC there. A 6 volt dry cell is plenty or I have used the smallest voltage I can get out of the generator starting batteries THROUGH a probe type test light so the lamp limits current flowing. In an emergency you can just scratch a wire on the terminals with the generator turning at full governed rpm and get it to go.

I am guessing you lost the residual from the vibrations resulting from the bad bearing or might have swapped the exciter field leads when reinstalling it and simply need to flash it.

If you have good residual or flashing doesn't cause voltage to build up AND STAY UP, then the other checks you mentioned need to be done. The exciter field or rotor or the main field on the rotor may be shorted from the parts scrubbing. disconnect the field from the rectifier heat sinks and test. If those are ok, the rectifier diodes will be arranged in two groups of 3 all same polarity and are usually stud mount type so you can easily replace them. To test each one you can remove the stud end from the heat sink. I replaced all three when I found any one bad. They are available from suppliers like DIGIKEY and MOUSER, sometimes eBay etc. Mainly match up the stud size and polarity and most any amperage and voltage will work and be better than what was originally installed. I think I wound up with 40 amp and 400 volt on an 85KR I fixed once.

OH......before you do all this, check the exciter breaker on the control panel isn't tripped. That would be can easy fix, but it may have tripped for a reason. If you need more troubleshooting, I can supply ONAN literature or its probably available online if you search for ONAN 900-0150 Service manual The wingspan site pdf file is what you want.
not sure if that model had a magnaciter or not. might try Smokestack onan generator forums.

D46U straight blade,D46U cat angle blade,allis chalmers AD4 grader and Khoering 404 dragline. D4C 40A,D4 2T and scraper.

Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 9:42 AM
ccjersey
Offline
Send a private message to ccjersey
Posts: 4,422
Thank you received: 0
X2 on SMOKSTAK SparksNArcs Onan section. Used to spend a lot of time there. There were more Onan guys than any other brand.

Probably a little too late to be a Magneciter, I think the last ones would have been before the early 1970's except I have a 25 kW PTO generator from then that is a magneciter............and they were all brush type.

So it will be a VR21 regulator board system. Not one of the most reliable regulators ever made, but very repairable. Everyone used to recommend Flight Systems to repair or exchange the VR21. Last I heard they were offering their own redesigned regulator to replace the VR21 if you want. www.flightsystems.com
D2-5J's, D6-9U's, D318 and D333 power units, 12E-99E grader, 922B & 944A wheel loaders, D330C generator set, DW20 water tanker and a bunch of Jersey cows to take care of in my spare time😄
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 9:57 AM
STEPHEN
Topic Author
Offline
Send a private message to STEPHEN
Posts: 2,461
Thank you received: 1
Reply to WA7OPY:
Did the exciter rotor rub the exciter field poles??? If so you will need to make friends with a motor rewind shop....WA7OPY

Well the ball separator lost its mind, and the bells were all grouped together. Luckily the inner ring is clamped and didn't spin. The laminations looked good.
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 10:49 AM
STEPHEN
Topic Author
Offline
Send a private message to STEPHEN
Posts: 2,461
Thank you received: 1
Reply to ccjersey:
Check for "residual" voltage on the output. Should be some AC voltage output from the stator windings before any output breaker etc. Usually anything over a few volts will build up if everything else is good. 0 or just a few volts you need to flash the field to boost it up. Many Onan manuals will have the procedure. Basically match polarity at connections to the exciter field leads and apply DC there. A 6 volt dry cell is plenty or I have used the smallest voltage I can get out of the generator starting batteries THROUGH a probe type test light so the lamp limits current flowing. In an emergency you can just scratch a wire on the terminals with the generator turning at full governed rpm and get it to go.

I am guessing you lost the residual from the vibrations resulting from the bad bearing or might have swapped the exciter field leads when reinstalling it and simply need to flash it.

If you have good residual or flashing doesn't cause voltage to build up AND STAY UP, then the other checks you mentioned need to be done. The exciter field or rotor or the main field on the rotor may be shorted from the parts scrubbing. disconnect the field from the rectifier heat sinks and test. If those are ok, the rectifier diodes will be arranged in two groups of 3 all same polarity and are usually stud mount type so you can easily replace them. To test each one you can remove the stud end from the heat sink. I replaced all three when I found any one bad. They are available from suppliers like DIGIKEY and MOUSER, sometimes eBay etc. Mainly match up the stud size and polarity and most any amperage and voltage will work and be better than what was originally installed. I think I wound up with 40 amp and 400 volt on an 85KR I fixed once.

OH......before you do all this, check the exciter breaker on the control panel isn't tripped. That would be can easy fix, but it may have tripped for a reason. If you need more troubleshooting, I can supply ONAN literature or its probably available online if you search for ONAN 900-0150 Service manual The wingspan site pdf file is what you want.
[quote="ccjersey"]Check for "residual" voltage on the output. Should be some AC voltage output from the stator windings before any output breaker etc. Usually anything over a few volts will build up if everything else is good. 0 or just a few volts you need to flash the field to boost it up. Many Onan manuals will have the procedure. Basically match polarity at connections to the exciter field leads and apply DC there. A 6 volt dry cell is plenty or I have used the smallest voltage I can get out of the generator starting batteries THROUGH a probe type test light so the lamp limits current flowing. In an emergency you can just scratch a wire on the terminals with the generator turning at full governed rpm and get it to go.

I am guessing you lost the residual from the vibrations resulting from the bad bearing or might have swapped the exciter field leads when reinstalling it and simply need to flash it.

If you have good residual or flashing doesn't cause voltage to build up AND STAY UP, then the other checks you mentioned need to be done. The exciter field or rotor or the main field on the rotor may be shorted from the parts scrubbing. disconnect the field from the rectifier heat sinks and test. If those are ok, the rectifier diodes will be arranged in two groups of 3 all same polarity and are usually stud mount type so you can easily replace them. To test each one you can remove the stud end from the heat sink. I replaced all three when I found any one bad. They are available from suppliers like DIGIKEY and MOUSER, sometimes eBay etc. Mainly match up the stud size and polarity and most any amperage and voltage will work and be better than what was originally installed. I think I wound up with 40 amp and 400 volt on an 85KR I fixed once.

OH......before you do all this, check the exciter breaker on the control panel isn't tripped. That would be can easy fix, but it may have tripped for a reason. If you need more troubleshooting, I can supply ONAN literature or its probably available online if you search for ONAN 900-0150 Service manual[/quote]

Thanks for your suggestions. The leads on the field were so long inside the cabinet that I didn't have to disconnect them. I did flip the exciter breaker a few times. Main thing is it was powering a big well pump before they quit with it. It been sitting at my shop for 2 or 3 months because I only have time to work on what is needed today. Got tired of looking at it fri afternoon & had a peek & a poke. I will try everyone's suggestions & see what happens. Thanks everyone!!!
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 10:58 AM
WA7OPY
Offline
Send a private message to WA7OPY
Posts: 217
Thank you received: 0
Reply to STEPHEN:
[quote="ccjersey"]Check for "residual" voltage on the output. Should be some AC voltage output from the stator windings before any output breaker etc. Usually anything over a few volts will build up if everything else is good. 0 or just a few volts you need to flash the field to boost it up. Many Onan manuals will have the procedure. Basically match polarity at connections to the exciter field leads and apply DC there. A 6 volt dry cell is plenty or I have used the smallest voltage I can get out of the generator starting batteries THROUGH a probe type test light so the lamp limits current flowing. In an emergency you can just scratch a wire on the terminals with the generator turning at full governed rpm and get it to go.

I am guessing you lost the residual from the vibrations resulting from the bad bearing or might have swapped the exciter field leads when reinstalling it and simply need to flash it.

If you have good residual or flashing doesn't cause voltage to build up AND STAY UP, then the other checks you mentioned need to be done. The exciter field or rotor or the main field on the rotor may be shorted from the parts scrubbing. disconnect the field from the rectifier heat sinks and test. If those are ok, the rectifier diodes will be arranged in two groups of 3 all same polarity and are usually stud mount type so you can easily replace them. To test each one you can remove the stud end from the heat sink. I replaced all three when I found any one bad. They are available from suppliers like DIGIKEY and MOUSER, sometimes eBay etc. Mainly match up the stud size and polarity and most any amperage and voltage will work and be better than what was originally installed. I think I wound up with 40 amp and 400 volt on an 85KR I fixed once.

OH......before you do all this, check the exciter breaker on the control panel isn't tripped. That would be can easy fix, but it may have tripped for a reason. If you need more troubleshooting, I can supply ONAN literature or its probably available online if you search for ONAN 900-0150 Service manual[/quote]

Thanks for your suggestions. The leads on the field were so long inside the cabinet that I didn't have to disconnect them. I did flip the exciter breaker a few times. Main thing is it was powering a big well pump before they quit with it. It been sitting at my shop for 2 or 3 months because I only have time to work on what is needed today. Got tired of looking at it fri afternoon & had a peek & a poke. I will try everyone's suggestions & see what happens. Thanks everyone!!!
Was it making power before you fix it,or was the loss of power why you check it out? With the cage gone on the bearing, the rotor would have been push hard into the field poles. It will make a lot of heat in a very short time, and ground the winding out. Find f1 and f2 and excite it with 6 to 12 volts DC keep track of the + and -. The ac should jump up above 60 volt all the way to 150 maybe higher. If the exciter is grounded you can kiss the vr good bye.If you know how disconnect f1 and f2 and meg the winding....WA7OPY
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 11:15 AM
STEPHEN
Topic Author
Offline
Send a private message to STEPHEN
Posts: 2,461
Thank you received: 1
Reply to WA7OPY:
Was it making power before you fix it,or was the loss of power why you check it out? With the cage gone on the bearing, the rotor would have been push hard into the field poles. It will make a lot of heat in a very short time, and ground the winding out. Find f1 and f2 and excite it with 6 to 12 volts DC keep track of the + and -. The ac should jump up above 60 volt all the way to 150 maybe higher. If the exciter is grounded you can kiss the vr good bye.If you know how disconnect f1 and f2 and meg the winding....WA7OPY


Doubt there is anyone at the farm to give me a timeline , all I know is I woke up with it parked in my driveway and a verbal that it was making bad noises. The usual.
We are onto the rock/root picker now. Bearings, roller chain & welding. "Gotta go, Joe". The usual- I love it.
Please log in or create an account to join the conversation.
Sun, Feb 17, 2019 11:47 AM
Showing 1 to 8 of 8 results
YouTube Video Placeholder

Follow Us on Social Media

Our channel highlights machines from the earliest Holt and Best track-type tractors, equipment from the start of Caterpillar in 1925, up to units built in the mid-1960s.

Upcoming Events

Cromford Steam Rally

Chapter Two

| Highacres Farm, Dewey Lane, Brackenfield, Derbyshire DE55 6DB, UK

The Century of Caterpillar

| Elkader, 203 Johnson St, Elkader, IA 52043, USA

100 YEARS OF CATERPILLAR IN TASMANIA

Chapter Nineteen

| 2 Winkleigh Rd, Exeter TAS 7275
View Calendar
ACMOC

Antique Caterpillar
Machinery Owners Club

1115 Madison St NE # 1117
Salem, OR 97301

[email protected]

Terms & Privacy
Website developed by AdCo

Testimonials

"I also joined a year ago. had been on here a couple of times as a non-member and found the info very helpful so I got a one year subscription (not very expensive at all) to try it out. I really like all the resources on here so I just got a three year. I think its a very small price for what you can get out of this site."
-Jason N

Join Today!