I think you're out of luck on the single phase 3 wire 120/240. That zig-zag connection is only possible on a 120/240 3 phase generator or at least it will result in 240/480 single phase 3 wire.
Best you can do with that one is to set it up for 240 volts (if that is even possible..........follow the output wires back into the generator connection box and see if you find 10 leads there that are spliced onto the 4 big ones that come out of the cabinet..) When set up for 240 volts, you will be able to pull 120 amps on 2 leads. When measuring voltage to the neutral, you will find that voltage at 139! If you need 120 volts, you can probably turn the voltage setting down and get 120/208 or you might want to stop at 127/220 which will not be too high on the "120" stuff and closer to 240 on the heavy circuits.
Or you can feed either 480 or 240 into a transformer with a center tapped secondary to get 120/240 three wire out.
Thanks for the help. I think I'll just wire it 208V 3 Phase and put a panel on it. I want to be able to power some light towers at shows and can split them up between the 3 legs.