Reply to ccjersey:
Probably not. You could use a transformer to step up from your highest voltage to 550-600.
Motors Frequency on the nameplate?
Are they 50 or 60 or 50/60 rated.
I remember 40 years ago, I was in a Plant with 440 Volts coming in, they had all 550/600 Volt motors in there.
There must have been a "Step-Up" transformer somewhere?
Now a days, it seems like a very uncommon voltage.
Just to counter ccjersey, you may possibly turn up the Voltage Regulator enough to get there.
Usual Disclaimer; provided the wiring was originally based on 600 Volt design and Ratings. Please have this checked by a Competant Authority.
Reason I say it might be "Do-Able" is because we do Voltage changes on Generators all the time. Most recent is a quantity of 75 Generators from Italy that came in at 600 Volts. The boys got really good at figuring out where 480 was on the voltage regulator potentiometer as these would shutdown on "Over Voltage" on startup!
One of next weeks projects will be a "Tap Changer" to provide 120/208 Wye or 277/480 Delta at full capacity just by setting the Switch prior to start up.