3306 Engine, 3 Phase Generator Conversion

3306 Engine, 3 Phase Generator Conversion

Showing 1 to 5 of 5 results
jgcox
Topic Author
Offline
Send a private message to jgcox
Posts: 5
Thank you received: 0
Question #1
I read a thread from 2012 stating that the 3306 is a very reliable engine.
Is the general consensus here still that the 3306 is a very good engine?
The one I'm looking at was built in the 1990s. It still SEEMS to be good.

Question #2
Can an old CAT gen-set configured for 120/208 3 phase be converted to 120/240 1 phase, i.e. 120-0-120 with 120 volts on each side of neutral that can be bonded to ground?

Any help would be appreciated.
Thanks,
JGC
Please log in or create an account to join the conversation.
Thu, Mar 10, 2016 9:02 AM
Rome K/G
Offline
Send a private message to Rome K/G
Posts: 6,092
Thank you received: 0
ya with a converter at the price of a whole generator, very pricey!
Please log in or create an account to join the conversation.
Thu, Mar 10, 2016 9:23 AM
BobPV15
Offline
Member
Send a private message to BobPV15
Posts: 100
Thank you received: 0
Reply to Rome K/G:
ya with a converter at the price of a whole generator, very pricey!
Yes I believe that the 3306 is a very good engine.

On question two, yes the 120/208 generator can be wired for 120/240 if all of the winding leads are brought out. But you only get 2/3rds of the power output.
So a 30 kva gen becomes a 20 kva gen.

Draw a triangle with the point at the top. mark the left side A the right B and the bottom C Now split the connection at the top and bottom of A
Move B & C down together and connect the top of B to the bottom of A.

Now the top of A is 120 the A-B connection is neutral and the bottom of C is your other 120!

Hope this helps
Please log in or create an account to join the conversation.
Thu, Mar 10, 2016 11:39 AM
jgcox
Topic Author
Offline
Send a private message to jgcox
Posts: 5
Thank you received: 0
Reply to BobPV15:
Yes I believe that the 3306 is a very good engine.

On question two, yes the 120/208 generator can be wired for 120/240 if all of the winding leads are brought out. But you only get 2/3rds of the power output.
So a 30 kva gen becomes a 20 kva gen.

Draw a triangle with the point at the top. mark the left side A the right B and the bottom C Now split the connection at the top and bottom of A
Move B & C down together and connect the top of B to the bottom of A.

Now the top of A is 120 the A-B connection is neutral and the bottom of C is your other 120!

Hope this helps
[quote="BobPV15"]Yes I believe that the 3306 is a very good engine.

On question two, yes the 120/208 generator can be wired for 120/240 if all of the winding leads are brought out. But you only get 2/3rds of the power output.
So a 30 kva gen becomes a 20 kva gen.

Draw a triangle with the point at the top. mark the left side A the right B and the bottom C Now split the connection at the top and bottom of A
Move B & C down together and connect the top of B to the bottom of A.

Now the top of A is 120 the A-B connection is neutral and the bottom of C is your other 120!

Hope this helps[/quote]

REPLY:
Yes - this is very helpful.

If I get the model and serial number of the alternator, is there a place I can look to see if "the winding leads are brought out"?
I'm guessing that to connect as you suggested, I would need 6 leads available - two for each of the 3 phases - yes???
Please log in or create an account to join the conversation.
Thu, Mar 10, 2016 9:07 PM
BobPV15
Offline
Member
Send a private message to BobPV15
Posts: 100
Thank you received: 0
Reply to jgcox:
[quote="BobPV15"]Yes I believe that the 3306 is a very good engine.

On question two, yes the 120/208 generator can be wired for 120/240 if all of the winding leads are brought out. But you only get 2/3rds of the power output.
So a 30 kva gen becomes a 20 kva gen.

Draw a triangle with the point at the top. mark the left side A the right B and the bottom C Now split the connection at the top and bottom of A
Move B & C down together and connect the top of B to the bottom of A.

Now the top of A is 120 the A-B connection is neutral and the bottom of C is your other 120!

Hope this helps[/quote]

REPLY:
Yes - this is very helpful.

If I get the model and serial number of the alternator, is there a place I can look to see if "the winding leads are brought out"?
I'm guessing that to connect as you suggested, I would need 6 leads available - two for each of the 3 phases - yes???
Usually there is a mounting plate for the connections, under that are the wires. Yes there will be at least 6 for the three phases and a couple of small ones that go to the voltage regulator. If it is a dual voltage generator there could be 12. There each phase is split in two and can be wired in series for high voltage or parallel for low voltage. When you get the generator model Google it and see what comes up. If you have a motor rewind shop near you they would know what to do.
Please log in or create an account to join the conversation.
Thu, Mar 10, 2016 11:51 PM
ccjersey
Offline
Send a private message to ccjersey
Posts: 4,422
Thank you received: 0
To reconnect for 120/240, you have to have 9 leads or 12 leads.

A 6 lead generator would be an odd thing to see, but if you were to reconnect a 120/208 3 phase 6 lead generator into a dogleg as described already, you would get approximately 208/416 single phase instead of 120/240.

There are two options for 12 lead generator ends. Dogleg (sometimes called zigzag .....mistake in my opinion) and double delta. Either one works just fine. The dogleg connection can be obtained from the 120/208 3 phase Y connection without even knowing what the lead numbers are, so that might be one reason to use it over the double delta, but the two are completely functionally equivalent.

CAT used to make mostly 9/10 lead dual voltage 3 phase Y generators. These are reconnectable by either paralleling the windings in 3 pairs for low voltage 208-240 or connecting them in 3 series circuits for high voltage 416-480 volts. In either case the windings remain in a Y configuration because the 10, 11 and 12 leads are permanently connected inside the stator and a single lead brought out for the neutral. A motor shop can cut into one of these 9/10 lead generators windings, split the Y and attach the 10,11,12 leads required for single phase reconnections. BUT this is no guarantee the exciter and regulator will function after the reconnections. Might have to go with aftermarket components to get that to go.

There is a single phase reconnection of the 9/10 lead Y type generators that is properly called the zigzag connection. Unfortunately it requires a rather rare 110-120/220-240 dual voltage 9 lead vs the more common 208-240/416-480 dual voltage 9 lead generator. Using the zigzag on the 208/416 generator produces 208/416 single phase.....not very useful!

With any of the single phase reconnections, the generator end can only produce 2/3 of the former 3 phase kVA rating UNLESS it was ordered as an extended stack option which has a larger than standard winding. This option typically allows single phase load equal to 3 phase kW rating
D2-5J's, D6-9U's, D318 and D333 power units, 12E-99E grader, 922B & 944A wheel loaders, D330C generator set, DW20 water tanker and a bunch of Jersey cows to take care of in my spare time😄
Please log in or create an account to join the conversation.
Fri, Mar 11, 2016 3:49 AM
Showing 1 to 5 of 5 results
YouTube Video Placeholder

Follow Us on Social Media

Our channel highlights machines from the earliest Holt and Best track-type tractors, equipment from the start of Caterpillar in 1925, up to units built in the mid-1960s.

Upcoming Events

Lake Goldsmith Steam and Vintage Rally

Chapter Nineteen

| 1234 Carngham-Lake Goldsmith Rd, Lake Goldsmith, Victoria, 3373, Australia

Stradsett Park Vintage Rally

Chapter Two

| Stradsett, Nr Downham Market. Norfolk PE33 9HA UK

Chapter 2 The Link Club's AGM

Chapter Two

| Faulkner Farm, West Drove, Wisbech, Cambridgeshire, PE14 7DP, UK

HAMILTON PASTURAL MUSEUM

Chapter Nineteen

| Cnr Hiller Lane and Ballarat Road, Hamilton, Vic, 3300
View Calendar
ACMOC

Antique Caterpillar
Machinery Owners Club

1115 Madison St NE # 1117
Salem, OR 97301

[email protected]

Terms & Privacy
Website developed by AdCo

Testimonials

"I also joined a year ago. had been on here a couple of times as a non-member and found the info very helpful so I got a one year subscription (not very expensive at all) to try it out. I really like all the resources on here so I just got a three year. I think its a very small price for what you can get out of this site."
-Jason N

Join Today!