The exciter motor on my new/used gen set has four wires coming out of it. 2 are grounded to the big generator and the other two run down to this modern box (c pic). Were do the 2 wires that run out of the box go to excite the big generator? The only place I see is to attach them is to the main leads. But which 2?
Attachment
Attachment
Attachment
Please log in or create an account to join the conversation.
Mon, Dec 10, 2012 12:03 PM
edb
Offline
Member
Send a private message to edb
Posts: 4,027
Thank you received: 0
Hi Mike,
will post these from previous discussions here.
Am no expert, just hope they will help you.
Cheers,
Eddie B.

Hope the order of post is good but attachment names and no's should get you there.
Attachment
Attachment
Attachment
Attachment
Attachment
Attachment
Attachment
Attachment
Please log in or create an account to join the conversation.
Mon, Dec 10, 2012 12:54 PM
ccjersey
Offline
Send a private message to ccjersey
Posts: 4,422
Thank you received: 0
Mike, I believe you were going to run this generator connected in the low voltage 3 phase Y connection as shown on the CAT tag. Each line out will be connected to 2 generator leads (1+7, 2+8, 3+9 with 4,5,6,0 for the neutral).


The usual plan for a reconnectable generator uses 7 & 8 for the regulator sensing, so when it's connected in series for high voltage, the 7 to 8 voltage is still the same ~208 volts it is when the windings are paralleled for low voltage.

The Basler regulator needs an AC voltage source to monitor ranging from 190 to 240 volts. So if you're running single phase off your generator, you'll be using two lines (1+7 and 2+8 for example). You want the regulator sensing the lines that have the load so the regulator is more responsive. So connect it to the same lines you are using for your single phase.
D2-5J's, D6-9U's, D318 and D333 power units, 12E-99E grader, 922B & 944A wheel loaders, D330C generator set, DW20 water tanker and a bunch of Jersey cows to take care of in my spare time😄
Please log in or create an account to join the conversation.
Mon, Dec 10, 2012 9:31 PM
Showing 1 to 2 of 2 results
YouTube Video Placeholder

Follow Us on Social Media

Our channel highlights machines from the earliest Holt and Best track-type tractors, equipment from the start of Caterpillar in 1925, up to units built in the mid-1960s.

Upcoming Events

Cromford Steam Rally

Chapter Two

| Highacres Farm, Dewey Lane, Brackenfield, Derbyshire DE55 6DB, UK

The Century of Caterpillar

| Elkader, 203 Johnson St, Elkader, IA 52043, USA

100 YEARS OF CATERPILLAR IN TASMANIA

Chapter Nineteen

| 2 Winkleigh Rd, Exeter TAS 7275
View Calendar
ACMOC

Antique Caterpillar
Machinery Owners Club

1115 Madison St NE # 1117
Salem, OR 97301

[email protected]

Terms & Privacy
Website developed by AdCo

Testimonials

"I became a member recently because the wealth of knowledge here is priceless." 
-Chris R

Join Today!